Seeking help with operational issues of the Caddley freezer

2019-04-15View Original

Thread Content

Our company’s utility systems are equipped with a Kaideli refrigerator. The operating condition is set at -10°C. The refrigerator and the buffer tank form an internal circulation system, while the buffer tank and the workshop heat exchanger constitute an external circulation system. No measures have been taken to regulate pressure or flow in the internal circulation system; however, there is a valve that controls the pressure before the fluid enters the buffer tank in the external circulation system. Ethylene glycol is used as the chilled water; the freezing point was measured to be -26°C using a freezing point detector, with a corresponding concentration of 42.2 and a density of 1.059. Recently, the refrigerant has shown unstable heat exchange efficiency, manifested in the following ways: 1) it takes longer to reach the temperature set by the system; 2) the temperature at the compressor’s outlet pipe is sometimes high (indicating good heat exchange and thus less time required) and sometimes at room temperature (indicating poor heat exchange and thus more time required); 3) more frost forms on the outside of the compressor compared to before; 4) the sight glass for the compressor’s refrigeration oil sometimes contains many bubbles and other times the liquid inside is relatively pure. The manufacturer now wants to determine separately what the temperature is when the chilled water reaches freezing point ; It is suspected that there are deposits or crystals on the outer wall of the heat exchange tube between the refrigerant and the chilled water. May I ask where the problem lies? What should a better solution look like? Thank you so much!
Reply #22019-04-16
The freezer has an approaching temperature. It is generally between 1.0 and 1.5 degrees. Above this value, you need to consider heat exchange. Whether the efficiency drop is caused by scaling or crystallization. Also, it is important to know whether the heat exchange in your workshop is continuous or intermittent. From an energy-saving perspective, for every 1-degree decrease in the inlet temperature of the cooling water, the energy consumption of the main unit for the same level of cooling is reduced by 3%. Does your water have a water treatment system to prevent scaling?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.