Help question: Calculation of the heat exchange area of a condenser

2020-07-20View Original

Thread Content

Our company is now planning to install a 5-ton distillation tank for vacuum distillation of water. The heat source is steam, with the temperature inside the tank ranging from 70 to 90°C. The vacuum pump has an exhaust capacity of 200 L/s. The condenser used in conjunction with this vacuum pump relies on circulating water as the cooling medium, with the temperature of this circulating water being between 30 and 32°C. The amount of water that can be distilled is 500 kg/h, and the condensation efficiency is around 90%. How should the heat exchange area of the condenser be calculated? Tube heat exchanger
Reply #22020-07-20
I came across it by chance and wanted to learn more about it; I hope someone knowledgeable can answer my questions
Reply #32020-07-21
It is necessary to know the flow rate of the heat source and its inlet and outlet temperatures, as well as the flow rate of the cold source and its inlet and outlet temperatures; 5 out of these 6 conditions are required. Additionally, pressure information is also needed
Reply #42020-07-21
You need to provide the temperature changes and flow rates of the heat source, as well as those of the cold source; only by providing this information can we carry out the calculations
Reply #52020-07-21
The heat source is steam at 0.25 MPa, while the cold source is circulating water with a flow rate of 20 m3/h and an inlet temperature of 30°C. The inlet temperature of the water vapor in the condenser is approximately 40–60°C, whereas the outlet temperature is below 35°C.
Reply #62020-07-21
The heat source is steam at 0.25 MPa, while the cold source is circulating water with a flow rate of 20 m3/h and an inlet temperature of 30°C. The inlet temperature of the water vapor in the condenser is approximately 40–60°C, whereas the outlet temperature is below 35°C.
Reply #72020-07-23
The condensed water vapor should flow through the shell side, while the cooling water flows through the tube side; the condenser should be placed horizontally, right? What is the operating pressure on the process side that is still missing? If it is pumped with a vacuum pump, it will definitely be in a vacuum state. Is it acceptable to use the saturated vapor pressure of water vapor at 40~60°C? Also, what is the flow rate of the non-condensable gases? What are the material requirements for heat exchange tubes?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.