2019-12-19View Original

Thread Content

Is it necessary to install a blowdown expansion vessel for a 4-ton boiler? If there are regulations, what size is appropriate to set? Please share your valuable suggestions; thank you!
Reply #22019-12-19
It can be connected directly to the sewage cooling tank; 0.8 m3 should be sufficient if one is needed.
Reply #32019-12-19
Generally, the drainage volume for regular and continuous drainage in steam boilers is controlled to be no more than 5% of the steam generation volume; therefore, the drainage volume in your case should not exceed 0.2 tons per hour, or 0.2 m³/h. The drainage tank requires gas-liquid separation, and based on a 1/3 design factor, the size of the drainage tank should be at least 0.6 m³.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.