Spacing requirements between liquid ammonia storage tanks and other equipment

2023-01-03View Original

Thread Content

This post was last edited by Chem-Design on 2023-1-3 at 15:36. I’m working on a project that is designed in accordance with petrochemical standards; there is a liquid ammonia tank area, and there’s also a Class A facility nearby. What should be the appropriate distance between the two?; It is the same as in the case of liquefied hydrocarbons regarding the spacing between liquid ammonia storage areas. It is not clear whether there are any regulatory requirements regarding the distance between liquid ammonia tanks and other equipment; should it be classified as a Class B flammable liquid or as a liquefied hydrocarbon? ; Seeking help from all the experts here ;
Reply #22023-01-03
GB50160 only specifies that the spacing between liquid ammonia storage tanks should be determined based on liquefied hydrocarbons; it does not require that the spacing from such tanks to other facilities be calculated using the same criteria. Table 2-4 in Document No. 115 of the \"Technical Specifications for Safe Production of Liquid Ammonia Storage and Loading/Unloading in Shandong Province (Trial Version)\” also specifies spacings based on Class B liquids
Reply #32023-01-04
66666666666666666
Reply #42023-01-04
This post was last edited by Chem-Design on 2023-1-4 at 09:39. Thank you for helping me out with the handshake issue; I checked it, and indeed it’s as you said; But the authorities have provided a response (see image); the general idea is to refer to local standards, yet those standards do not specify requirements regarding the distance from other buildings. How should this be interpreted? ;
Reply #52023-01-06
Why is it Category B? Ammonia lightning: -54°C (CC) ; Saturated vapor pressure 0.5 MP (4.7°C)
Reply #62023-01-09
GB50160-2008 (2018 edition), Clause 3.0.2 – Table 2A: Liquid ammonia is present; Ammonia is listed under Category B in the explanatory notes to the current building codes.
Reply #72023-01-10
The liquid ammonia tank area may be considered a major hazard source; please comply with the corresponding fire separation requirements
Reply #82023-07-10
For the liquid ammonia storage area, it’s necessary to first assess it based on the criteria for identifying major hazard sources; there is a high probability that it will be classified as such. In that case, all design specifications must take into account the requirements related to major hazard sources

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.