Can any kind of exhaust gas from chemical processing units be sent to the flare system?

2025-10-12View Original

Thread Content

Principles for the installation of flare systems
I. Relevant standards and regulations: “Fire Protection Design Code for Petrochemical Enterprises (2018 edition)” GB50160-2008, “Design Code for Flammable Gas Emission Systems in Petrochemical Industries” SH 3009-2013, “Installation of Flare Systems” HG/T 20570.12-1995
II. Standard requirements:
(1) Article 5.5.4 of the “Fire Protection Design Code for Petrochemical Enterprises (2018 edition)” GB50160-2008 stipulates that the outlets of safety valves on equipment handling flammable gases and liquids must comply with the following requirements: 2. The discharge pipes connected to the safety valves of equipment handling flammable gases should be connected to the flare system or other safety discharge facilities; 3. Combustible gases or liquids that may ignite immediately after release should be cooled before being connected to the venting facilities ; 4. Combustible gases that may contain liquid droplets should be routed to the flare system after passing through a liquid separation tank. Article 5.5.7 requires that Class A, B, and C equipment shall be equipped with emergency discharge facilities for accidents, and shall comply with the following provisions: 1. For equipment handling liquefied hydrocarbons or flammable liquids, it must be possible to discharge such hydrocarbons or liquids from the equipment to a safe location, with any remaining amount being discharged into a flare ; 2. For combustible gas equipment, it should be possible to vent the combustible gas inside the equipment into a flare or a safe venting system. Article 5.5.15 requires that liquids, combustible gases with low calorific value, combustible gases containing oxygen or halogen elements and their compounds, combustible gases with extremely high or high toxicity, inert gases, acidic gases, and other corrosive gases shall not be discharged into the plant-wide flare system; instead, separate emission systems or systems for treating such emissions must be installed. (Explanation of the provisions of this article: Discharging combustible gases with a low calorific value into the flare system can disrupt the stable combustion of the flare or cause it to go out) ; The release of oxygen-containing flammable gases into the flare system can result in the formation of explosive gases within that system and its facilities, which may lead to backfire and explosions, as well as damage to pipes or equipment ; Acidic gases and other corrosive gases can cause air pollution as well as corrosion of pipelines and equipment; therefore, a separate acidic gas flare should be installed. For gases with extreme or high toxicity or those containing corrosive substances, having separate treatment and emission systems in place helps ensure safe production. The toxicity classification should be determined in accordance with the current standards, namely **“Classification of Hazards from Occupational Exposure to Toxic Substances” GB 5044 and the “List of Highly Toxic Substances” (Document No. Wei Fa Jian Fa 142)**. However, benzene and carbon monoxide emitted by petrochemical enterprises lose their toxicity after being fully burned in a flare system; therefore, such substances or flammable gases containing them can still be discharged into a public flare system. )( 2) Article 4.3 of the \"Design Code for Flammable Gas Emission Systems in Petrochemical Industries\" SH 3009-2013 requires that no various liquids shall be discharged into the plant’s flammable gas emission system. Article 4.4 requires that combustible gas containing asphalt, residue oil, powder, or solid particles be separated and treated within the facility before being released. Article 4.5 requires that combustible gas streams containing hydrocarbons of C5 or higher grade, or water vapor, be passed through a liquid separation tank prior to discharge, in order to remove liquid droplets with a size of 600 um or larger. Section 5.1.4 requires that an acidic gas emission system be installed separately. Article 5.2 stipulates that gases which can be discharged into the plant-wide combustible gas discharge system: Gases from the following various sources in 5.2.1 may be discharged into the plant-wide combustible gas discharge system: a) Combustible gases that cannot be utilized by the production facilities and must therefore be discharged ; b) Flammable gases released due to accident venting or safety valve operation ; c) Flammable gases emitted during startup, shutdown, and maintenance operations ; d) Flammable gases discharged intermittently over short periods of time, such as those from liquefied petroleum gas pumps ; e) Toxic, harmful, and flammable gases emitted from production equipment, containers, etc. 5.2.2 Gases with a calorific value lower than 7880 kJ/Nm3 shall have their calorific value adjusted before being discharged into the plant’s flammable gas emission system.
Reply #22025-10-12
Article 5.3 requires that gases which should not be discharged into the plant’s overall flammable gas emission system must not be released into it; instead, they should be sent to specialized emission systems or treated separately: a) Gases that can undergo chemical reactions with the substances present in the flammable gas emission system; b) Flammable gases that are prone to polymerization and have an adverse effect on the flow capacity of the exhaust system pipes ; c) Flammable gases with an oxygen content greater than 2% (v%) ; d) Gases of highly toxic media (such as hydrogen cyanide) or corrosive media (such as acidic gases) ; e) It is more economical and safer to process flammable gases within the unit rather than discharging them into the plant-wide flammable gas discharge system ; f) The maximum allowable discharge backpressure is low, allowing the discharge of gases that pose safety risks to the plant’s flammable gas emission system. (Interpretation of the provisions, d) On the one hand, if highly toxic substances are released into the atmosphere as a result of incomplete combustion, the hazards they pose are extremely severe ; The material of the exhaust pipes for gases containing corrosive media must be corrosion-resistant. On the other hand, under normal production conditions, the combustible gases in the main pipeline network of the plant’s combustible gas emission system need to be recovered for use as fuel gas; gases that are highly toxic or contain corrosive substances are not allowed to enter. f) The plant’s flammable gas emission system is a type of unorganized emission system. In the event of an accidental release, the high pressure generated will prevent low-pressure gases from entering. Therefore, there is a safety risk associated with low-pressure flammable gases from such production units, which require continuous emission but cannot tolerate short-term pressure buildup, entering the plant’s flammable gas emission system. ) 5.3.2 When only individual units in the entire plant emit small amounts of gases containing highly toxic or corrosive substances, it is advisable to install treatment facilities within those units. (3) According to Article 2.0.1.3 of \"Torch System Design\" HG/T 20570.12-1995, the exhaust gases from the torch main pipe are classified into the following four categories based on the state of the medium: a. Hot gases (t>0℃, with or without water) ; b. Cold gas (t
Reply #32025-10-12
Summary: 1. Based on the state of the emitted medium: (a) Hot gas (t>0℃, with or without water); b. Cold gas (t
Reply #42025-10-12
【Ten Years of Rapid Development in Chemical Equipment】2727–2025: High pressure to reach 10 MPa! Zhongneng Dayou has successfully developed a multi-field coupling testing device for hydrogen production using 100kW-class PEM electrolyzers. https://bbs.hcbbs.com/thread-5702702-1-1.html (Source: Haichuan Chemical Industry Forum)
Reply #52025-10-12
【Ten Years of Rapid Development in Chemical Equipment】2727–2025: High pressure to reach 10 MPa! Zhongneng Dayou has successfully developed a multi-field coupling testing device for hydrogen production using 100kW-class PEM electrolyzers. https://bbs.hcbbs.com/thread-5702702-1-1.html (Source: Haichuan Chemical Industry Forum)
Reply #62025-10-13
【Ten Years of Rapid Development in Chemical Engineering Equipment】From 2027 to 2025, CNPC Pipeline Bureau successfully developed an intelligent anti-corrosion construction robot for storage tank exteriors. https://bbs.hcbbs.com/thread-5702707-1-1.html (Source: Haichuan Chemical Industry Forum)
Reply #72025-10-13
【Ten Years of Rapid Development in Chemical Equipment】The first AI optimization model for methanol distillation units in China was put into operation at Yulin Energy Chemical Complex in Shaanxi from 2029 to 2025. https://bbs.hcbbs.com/thread-5702720-1-1.html (Source: Haichuan Chemical Forum)
Reply #82025-10-14
【Ten Years of Rapid Development in Chemical Equipment】The first AI optimization model for methanol distillation units in China was put into operation at Yulin Energy Chemical Complex in Shaanxi from 2029 to 2025. https://bbs.hcbbs.com/thread-5702720-1-1.html (Source: Haichuan Chemical Forum)
Reply #92025-10-14
【Ten Years of Rapid Development in Chemical Equipment】2730-2025: The world’s first set! New breakthrough achieved in the pilot plant for producing acid and cement from third-generation phosphogypsum https://bbs.hcbbs.com/thread-5702721-1-1.html (Source: Haichuan Chemical Industry Forum)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.