In Table 8.3.9 of GB50187, Note 3 states that for pipelines and pipe racks carrying liquefied hydrocarbons, flammable liquids, or flammable gases, the minimum horizontal distance from such pipelines and pipe racks to buildings and structures should also comply with the requirements of **current relevant design standards. Which standard exactly needs to be met here? Which provision applies? ?
Chapter 8 of the General Plan Code, in particular the two charts in Chapter 8 of GB 50187-2012 Code for General Plan Design of Industrial Enterprises
Sir, I’m asking whether the distance between flammable liquid pipelines and buildings must comply with the current **standards and regulations**. Which specific standards and regulations are referred to here? ?
For hydrogen, refer to the specifications for hydrogen stations; for natural gas, refer to the regulations for gas stations; for oxygen, refer to the guidelines for oxygen stations. In fact, it is carried out according to the table provided in the specifications. However, all the aforementioned standards stipulate that they must not be installed together with cables and wires; yet in the chemical industry, it seems that they are often installed together. Therefore, for co-installation, that is, laying cable trays over pipelines carrying natural gas or hydrogen, it is, in principle, in violation of GB/T20801
Chapter 8 of the General Plan Code, in particular the two charts in Chapter 8 of GB 50187-2012 Code for General Plan Design of Industrial Enterprises