In accordance with Article 6.2.24 of GB50160-2008, the feed pipe of a storage tank shall be connected to the lower part of the tank body; if connection from the upper part is necessary, it should extend to a distance of 200 mm from the bottom of the tank. ” If connecting from the bottom, is it sufficient to insert it horizontally, or does it require a bend at the pipe end pointing downward after horizontal insertion? Urgently need help, thanks!
Reply #22017-06-05
It is best to make a bend at the pipe end with it facing downward after entering horizontally
Reply #32017-06-05
It seems that neither of the above two options is scientific; I’ve found that it should be a “diffusion-type oil inlet pipe”.
Reply #42017-06-05
We use horizontal feeding (internal floating roof tank with diffuser tank), with discharge through elbows.
Reply #52017-06-05
If a flammable liquid is being poured into the tank, a pressure relief pipe can be used at a vertical distance of 200 mm from the center of the tank bottom; once the pipe is inserted into the tank, it should have holes made at 120-degree angles to allow pressure release. If it is necessary to introduce the pipeline from above into the tank, a elbow should be used at a distance of 200 mm plus the pipe diameter from the center bottom of the tank to convert it into a horizontal pipeline; thereafter, a diffuser or a 120-degree perforated pressure-relief pipe should be employed in the design. It is recommended to use a 120-degree perforation for liquid injection, as it offers good cost-performance and complies with the standards! {The length of the horizontal pipe inside the tank should not exceed 2/5 of the tank’s diameter}
Reply #62017-06-05
Stop bending the pipes to prevent severe erosion
Reply #72017-06-06
Enter horizontally, with a diffusion tube inside

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.