I would like to ask everyone: should control valves be installed in front of or behind the flow meter? Are there any requirements or principles involved?
The flow meter should be installed behind the control valve (if you want to know the flow rate after regulation). And it meets the installation requirements for flow meters.
The flow meter should be installed behind the control valve (if you want to know the flow rate after regulation). And it meets the installation requirements for flow meters.
Flow meters should generally be installed upstream of control valves, primarily to prevent the disturbances caused by the control valves on the flow pattern from affecting the metering accuracy. Reference can be made to GB 50096 \"Code for Installation of Automatic Instruments\".
Can the flow meter only be installed behind the control valve, or can it be installed anywhere? How is there someone saying it should be installed at the front?
I agree with what was said on floor 4: flow meters should generally be installed upstream of control valves, mainly to prevent the disturbances caused by the control valves on the flow pattern from affecting the meter’s measurements.
I agree with what was said on floor 4: flow meters should generally be installed upstream of control valves, mainly to prevent the disturbances caused by the control valves on the flow pattern from affecting the meter’s measurements.
I agree with what was said on floor 4: flow meters should generally be installed upstream of control valves, mainly to prevent the disturbances caused by the control valves on the flow pattern from affecting the meter’s measurements.
I agree with what was said on floor 4: flow meters should generally be installed upstream of control valves, mainly to prevent the disturbances caused by the control valves on the flow pattern from affecting the meter’s measurements.
Upstream of the control valve, someone upstairs has already explained the reason