Tank level gauge

2017-09-25View Original

Thread Content

Sometimes there are two liquid level gauges in the storage tank that will alarm high, and sometimes there will be one high alarm and one low alarm. Why is this like this? What a design concept! Welcome to discuss with each other
Reply #22017-09-25
Regarding your question, it is recommended that you refer to 5.4.1~5.4.5 and 6.3.2~6.3.4 of the "SHT3007-2014 Tank Area Design Specifications for Petrochemical Storage and Transportation Systems" for your reference.
Reply #32017-09-26
GB50074-2014 Article 15.1.4: The liquid level measuring instrument used for the high and low liquid level alarm signals of the storage tank should use a separate continuous liquid level measuring instrument or liquid level switch, and alarms and interlocks should be set in the automatic control system.
Reply #42017-09-26
For pressure vessel liquid level measurement, if two remote liquid level gauges are installed and there is no local liquid level gauge, is it non-compliant according to this requirement?
Reply #52017-09-27
It is illegal according to the regulations. for your information

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.