Issue with isolation valves on pipes for the inflow and outflow of flammable liquids

2017-11-17View Original

Thread Content

Our company’s storage tanks for flammable liquids are required to be equipped with emergency shut-off valves on their inlet and outlet pipelines. We use bottom feeding and bottom discharging; in this case, can the inlet pipeline and the outlet pipeline share one emergency shut-off valve? Thank you!
Reply #22017-11-17
What if feeding and discharging occur simultaneously?
Reply #32017-11-17
The emergency shut-off valve is primarily used to disconnect the tank from the outside, and its use is likely to fail approval.
Reply #42017-11-17
Our storage tank feeding and discharging occur at different times.
Reply #52017-11-17
I think it’s fine if they’re not done at the same time; consult the security department again.
Reply #62017-11-17
Since the inlet and outlet pipes are separate, the emergency shut-off valves cannot be shared, right?
Reply #72017-11-18
I can do it too; many people do it this way
Reply #82017-11-18
It should be possible; Because during design, the incoming and outgoing materials share the same pathway ; Its function is to disconnect and isolate the storage tank from the outside world in emergency situations ; It is not common for a tank to have materials entering and exiting it at the same time; generally, designs include dynamic tanks and static tanks ; At least one in use and one as a backup ;
Reply #92017-11-18
We use 2. Everyone uses their own.
Reply #102017-11-18
If the inlet and outlet pipes are the same, installing a shut-off valve should work. In fact, in terms of reliability, it is not only necessary to install them, but you are also advised to use dual valves. I set it up in this way in the unit’s tank area. After all, the possibility of both valves leaking at the same time is very low.
Reply #112017-11-21
A cut-off valve is provided for discharge; one seems not necessary for feed.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.