How to calculate the gas consumption for control valves

2018-05-09View Original

Thread Content

There is a system that includes a dozen or so pneumatic on/off valves and two pneumatic control valves; what is the required amount of compressed air, and how is it calculated?
Reply #22018-05-12
It can be estimated as follows: 1) Based on the control valves, each control valve consumes 1–2 Nm3/h of air; 2) For the pneumatic instruments in the control room, each one consumes 0.5–1 Nm3/h; 3) Each pneumatic instrument at the site consumes 1 Nm3/h of air.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.