Can the fire roads in a factory complex be blocked?

2018-06-08View Original

Thread Content

I’m seeking advice from experts. There is a chemical plant layout in which the circular fire road within the plant is interrupted by factory buildings; no other way seems to exist to resolve this issue. Therefore, I was wondering whether it would be possible to create two turnaround areas on that interrupted fire road, using them as dead-end fire roads The factory complex has two entrances and exits. Once the fire access road is blocked, access to the factory buildings on the front side is possible only through the front door, while access to the factory buildings at the back requires using the road outside the factory via the back door. I’m not sure whether such a change violates the regulations I’m looking for recommendations on fire road standards; so far I’ve only reviewed the requirements regarding fire roads in the building codes. The factory building has an area of less than 3,000 square meters and is classified as a Class A building; according to the construction regulations, it is not necessary to have a circular fire road. Also, there is only this one main road throughout the entire factory area. I need help – is such a change reasonable? Looking for fire road design codes or internal factory road design codes! Thank you!
Reply #22018-06-08
There’s also GB50160; building codes may be updated soon, so keep an eye on that.
Reply #32018-06-08
There should be two main roads; it’s acceptable to not have a circular fire access route, as long as the fire radius meets the requirements
Reply #42018-06-08
I personally suggest that the original poster post a floor plan so everyone can take a look and help analyze it
Reply #52018-06-09
There are too few fire exits, and it’s even more unreasonable that they are occupied
Reply #62018-06-12
The fire protection radius can be met; the factory area is narrow and elongated, and the expansion of the building in the middle has interrupted the road
Reply #72018-06-12
The plant site is a small-scale chemical plant, consisting of one factory building, one warehouse, and one raw material storage area. There is only one main road, two entrances and exits. The fire access road is dead-ended, and there is a 12*12 meter turnaround area. Now that part of the road is occupied, I’m thinking of building two parking lots; I’m not sure if that’s feasible. Thank you to all the experts for their advice
Reply #82018-06-12
I’ve really never encountered this before; I’m quite curious and looking forward to the discussion

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.