2018-08-02View Original

Thread Content

This question. See: https://wenku.baidu.com/view/12fd5653f01dc281e53af022.html In this article, the pressure in the outlet pipe of the steam safety valve is still 0.3 MPa gauge. That’s where the problem lies. Generally, export pipelines are classified as non-pressure pipelines. . . . Please, those who know something should talk.
Reply #22018-08-02
It’s not a pressure pipeline – are you planning for a pressure lower than 0.1 MPag?
Reply #32018-08-03
This post was last edited by Liu Suifeng on 2018-8-3 06:43. The experimental data show that the pressure in the outlet pipeline is 0.3 MPag. That’s why there is this problem. If it is 0.3, then the design pressure of the outlet pipe must be higher than 0.1 as well
Reply #42018-08-03
Let’s rephrase the question: I would like to know what the operating temperature and pressure, as well as the design temperature and pressure, are for the outlet pipeline of your steam safety valves Just use steam at a certain level.
Reply #52023-08-12
The original link is no longer valid. I understand that the pressure at the outlet of the safety valve will be lower than the pressure at the inlet, but it usually doesn’t decrease by much. Considering the pressure loss in the drain pipe as well, the actual pressure loss is very small; therefore, the pipeline at the outlet of the safety valve should also be considered a pressure pipeline.
Reply #62023-08-12
After all, the outlet pipeline of the safety valve is short; the outlet pipe of the safety valve is of the same grade as or slightly lower than the inlet pipe, so the cost is not high, and it’s safe;
Reply #72023-08-12
The document cannot be opened. How long is the outlet pipe? Is it too long? After all, it leads to a discharge point

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.