Fire separation distance between the power distribution room and Class A factories

2018-08-26View Original

Thread Content

I would like to ask: Regarding the fire separation distances between high and low voltage substation rooms in factory areas and Class A factories as well as Class A warehouses, which provision of the building codes should be applied? Should it be Article 3.5.1 of the building codes, which stipulates that the fire separation distance between Class A warehouses (>10 tons, per item 1.2.5.6) and open-flame sources is 30 meters, or should it be Article 3.4.1, which specifies that the distance between Class A factories and outdoor substations and transformers is 25 meters?
Reply #22018-08-28
It’s better to use a longer distance; the safety factor is higher that way
Reply #32018-08-28
This should be calculated based on indoor conditions; I think neither of these two options applies. Clause 3.3.8 applies – it stipulates that the device should not be located adjacent to other elements, nor within an area prone to explosions. It depends on how the explosion-risk areas for Class A devices are defined in your case. It becomes clear by looking at clause 5.3.5 of GB50058.
Reply #42018-08-29
The explanation on the 3rd floor was quite clear. As a supplementary point regarding fire separation distances: for Class A warehouses, higher standards apply, and in accordance with Article 3.5.1 of GB50016, the distance from such warehouses to factories should be 15 meters; If it is a Class A workshop, Article 3.4.1 of GB50016 shall be applied: the distance between Class A workshops and Class C workshops should be 12 meters, provided that this is within an area free from explosion hazards.
Reply #52018-09-05
It’s so scary – it’s already over ten meters long; isn’t that misleading for people? First, determine which category Class A falls under, and decide whether the power distribution uses a dry-type transformer or an oil-type transformer. Then, Class A factories and Class A warehouses should apply the relevant provisions of 3.4.1 and 3.5.1 respectively

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.