Question for help: Under what circumstances should a bypass be installed for safety instruments? ! !

2020-04-21View Original

Thread Content

Guys, is the bypass optional or must it be removed?
Reply #22020-04-21
Safety instruments are generally used independently, and the relevant measurement points cannot be shared. What is the purpose of this bypass?
Reply #32020-04-21
You can refer to GBT50770 – basic process control should not interfere with the safety instrumented system. I’m not sure what purpose this bypass serves; please verify it in accordance with the standards
Reply #42020-04-23
This design was adopted for early startup because the system positioners at that time did not have a PST function; the bypass was designed for valve testing.
Reply #52020-04-24
It’s not clear what purpose this bypass actually serves The on/off valve on the main pipeline also lacks front and rear valves; if it breaks, the machine must be stopped in order to carry out repairs.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.