For organic waste gas pipelines with a flow rate of 350 cubic meters per hour, should the pipe flame arrester be DN150 or DN125?

2022-11-26View Original

Thread Content

For an organic waste gas pipeline with a flow rate of 350 cubic meters per hour, should a pipe flame arrester of DN150 or DN125 be used? What is the appropriate flow velocity inside the flame arrester?
Reply #22022-11-26
At a low gas flow rate of 10 meters per second, and with only a DN100 discharge diameter, a pipe flame arrester of DN125 is sufficient.
Reply #32022-12-05
Is the dielectric category IIA, IIB3, or IIC? Does a flame arrester prevent deflagration or detonation? What is the maximum allowable voltage drop? I can help you calculate it
Reply #42022-12-05
The medium is benzene IIBT4; it must be resistant to bombardment, and the lower the pressure drop, the better – ideally below 100 Pa. Thank you
Reply #52022-12-05
Benzene belongs to Group IIA. The graph above shows the flow pressure drop curve provided by the foreign brand PROTEGO for their flame arrestors. It can be seen that the pressure drop of a DN100 flame and detonation arrestor at a flow rate of 350 m3/h is approximately 700 Pa, while the pressure drop of a DN150 flame and detonation arrestor at the same flow rate is around 170 Pa. The pressure drop for DN125 is somewhere between the two, and it is not provided in the sample. So it depends on the allowable pressure drop you are willing to accept. If a pressure drop of around 300 pa to 400 pa is acceptable to you, then a DN125 flame arrester can be used ; If you want the pressure drop to be as low as possible, then you can use a flame arrester with a DN150 size, whose pressure drop is approximately 170 Pa. If it is absolutely required that the pressure drop be less than 100 Pa, then a flame arrester with a larger diameter (DN200 or above) must be used. Products of the same specification from domestic brands may have a slightly greater pressure drop; therefore, if using domestic brands, it is recommended to choose flame arresters with a larger diameter.
Reply #62022-12-05
Sure, my WeChat ID is football6

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.