How to convert 1700W for the ammonia cooler into ammonia consumption in KG: inlet temperature 10 degrees, pressure 1.6 MPa; outlet temperature -0.032 MPa, temperature 38 degrees

2022-12-17View Original

Thread Content

This post was last edited by MYT_iEAa5 on 2022-12-17 at 16:19
Reply #22022-12-29
Heat of vaporization: 1336.97 kJ/kg at the boiling point. The specific heat capacity at constant volume of the gas is 1.624 kj/(kg•K) at 25°C. 1.624*48=78; 1.700/(1337+78)=1.2 kg/s, which equals 4.3 tons/h
Reply #32023-02-02
Could you explain the meaning of each term in the formula?
Reply #42023-02-02
“1.624*48=78” This is the calculation for sensible heat; specific heat * weight * temperature difference. 1336.97 kj/kg is the latent heat

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.