I seek expert clarification on how DCS (or PLCs) communicate with Siemens PLCs through the EM277 DP communication module. Does the slave need to be programmed?
Reply #22017-02-03
The upper-level computer requires a corresponding communication card and programming, while the lower-level computer also needs programming and a communication card
Reply #32017-02-03
Your EM277 should act as a PROFIBUS SLAVE, with the DCS being the MASTER. In DCS, it is necessary to import the GSD file for the EM277, which can be downloaded from Siemens’ official website. Then configure IB and QB in DCS, corresponding to the V memory area of the S7200 CPU. Then, in MIRCO/WIN, store the data you want to communicate over in the corresponding V storage area.
Reply #42017-02-05
I’m currently working on DP communication; I’ll share some materials with you – just follow the instructions, it’s very simple. http://blog.sina.com.cn/s/blog_4b48c5250102w8jk.html
Reply #52017-02-07
Thank you very much; I have downloaded it from Zhenzaixue*

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.