Problems with valve limit switches (travel switches) in PSA hydrogen production

2017-04-16View Original

Thread Content

Recently, the valve travel switches (position switches) in the company have been giving false alarms frequently (once or twice a week), or the signals are lost. Passive magnetic induction switches are being used; the valves operate with linear motion, and the switches detect the position of the push rod in the upper cylinder. I would like to ask everyone: for such large quantities of programmable valves, which manufacturers’ valves and controls do you use, and what is the installation method? Thank you
Reply #22017-04-16
NAMUR signal, suitable for high-frequency switching applications.
Reply #32017-04-16
Valves from West China Hospital in Chengdu, switches from P+F! It’s possible that the position of the proximity switch isn’t adjusted properly! Generally, the proximity switch probe is 3-5 mm away from the sensing position.
Reply #42017-04-16
We were originally installed by Huaxi, and there are sometimes alarms as well
Reply #52017-04-16
Almost all of them, just like you, are magnetic induction switches
Reply #62017-04-17
Are there any pictures of magnetic induction switches that use mechanical proximity switches?
Reply #72017-04-17
West China seems to have a high market share; we are also from Shanghai West China
Reply #82017-04-17
No matter what brand the switch is, the key is to adjust the gap properly. Previously, my company had some faulty units; buying original ones was too expensive, so we simply opted for the cheapest domestic alternatives, which cost just over a dozen yuan. They worked fine for over a year without any problems.
Reply #92017-04-17
We use P+F position switches with NAMUR signals; such switches have requirements regarding the installation distance, as an unstable signal will occur if they are installed at the critical distance. Another factor is the ambient temperature; we have encountered cases where the switch failed after being exposed to direct sunlight for a long time during summer.
Reply #102017-04-17
Mine is from West China University; it’s from Chengdu West China University (Huake). The limit switch has been adjusted, but after two months it gradually loosens on its own. I think there’s something wrong with this type of connection

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.