2017-05-26View Original

Thread Content

The CPU of the Siemens PLC system is giving an alarm; there is a low battery voltage in the power supply. I would like to know whether this CPU alarm is caused by the power supply issue Can the battery of the power supply be replaced while it is in use, and how? What is the specific model number?
Reply #22017-05-26
Electrical failures can sometimes be incredibly unpredictable
Reply #32017-05-26
It’s the backup battery for the program inside the PS power supply module that needs to be replaced; it can be replaced while the system is still running. The battery triggers an alarm when its voltage drops below 2.7VDC, at which point it needs to be replaced. These are probably from the same batch; if you need to replace them, replace them all at once.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.