Problems with differential pressure transmitters for hot coal tank levels

2017-07-02View Original

Thread Content

At our company, we use capillary double-flange level gauges for measuring the level in hot coal and flash tanks in our polyester production processes. The design specifies the use of 704 silicone oil, but none of these gauges provide accurate readings. We have also attempted to use insulation for the capillaries, but that didn’t help either. I would like to ask those who work in this industry: what type of silicone oil do you use?
Reply #22017-07-04
To be honest, it has little to do with silicone oil filler. First, please provide the density of your medium and the flange spacing so that I can calculate the differential pressure value for you; after that, let me know what the medium being measured is I’ll help you choose the diaphragm; once that’s done, let me know the temperature and pressure of your medium so I can select the appropriate silicone oil for you! By the way, which factory is it from?
Reply #32017-07-05
An inaccurate reading from the instrument shouldn’t be closely related to the silicone oil used for filling; rather, it is the temperature being measured that affects the type of oil used for filling. I wonder if the original poster is interested in knowing what kind of oil is used in this industry Still looking to solve the problem of inaccurate instrument readings? If the issue is inaccurate instrument readings, please provide specific operating condition details
Reply #42017-07-06
There are many reasons for inaccurate measurements, but the type of oil used generally doesn’t have a significant impact. For silicone oil, temperature is the main factor to consider; if it isn’t resistant enough to high temperatures, it would have broken down long ago. Another reason is the measurement range and migration settings; measurement issues have also arisen due to insulation problems, cooling issues, as well as problems inherent in the equipment’s design and manufacturing process.
Reply #52017-07-06
This post was last edited by liu530014416 on 2017-7-6 22:51. Flash evaporation? Negative pressure? Double flanges cannot be used on vacuum tanks. What medium? Use foreign universal magnetostrictive level gauges.
Reply #62017-09-18
The effects of vacuum level and temperature on silicone oil need to be considered. But as far as I know, using double flanges in polyester polycondensation can cause problems, but I haven’t heard of any issues with them in other types of equipment
Reply #72017-09-18
Check if it’s a problem with the installation – is the transmitter installed on the high-pressure side? Also, check regarding migration and whether the ranges are correct.
Reply #82017-09-18
Using this medium with this device is the right choice; if that doesn’t work, switch to a magnetic flap
Reply #92017-09-19
Silicone oil merely serves to transmit pressure; to describe the specific operating conditions, consider replacing it with a magnetostrictive level gauge, which can be installed either from above or from the side.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.