HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Can the 8200D vortex flow meter reset its sensor?

2017-07-26View Original

Thread Content

There is a control valve on a pipeline; in front of this valve, there is a orifice flow meter as well as an vortex flow meter. The control valve is in its fully closed position, so the flow rate measured by the orifice flow meter is zero. However, the vortex flow meter shows a flow rate of 15%. Now, it is necessary to reset the flow rate measured by the vortex flow meter – how should this be done?
Reply #22017-07-26
Is there no one? Please, expert, tell me how to do it
Reply #32017-07-26
1. Is the valve fully closed? A flow rate of 0 on the orifice plate does not mean that the actual flow rate is also 0; it is advisable to perform a zero-point check using the orifice plate. 2. Check whether there is vibration in the pipeline; if so, try to eliminate it. 3. Determine whether the flow rate at 15% of the maximum value remains stable. You can adjust the control valve slightly to see if this flow rate changes, and whether it varies in proportion to the degree of opening of the control valve. 4. If it is confirmed to be true zero drift, zero cutting can be performed temporarily; it is not a full reset
Reply #42017-07-26
I’ll go give it a try tomorrow. By the way, that ‘zero cut’ – do you mean signal suppression?
Reply #52017-07-26
The pipeline experiences some vibration, but it’s not severe
Reply #62017-07-26
The Yokogawa DY has a vibration suppression function, which is excellent; I have used it. I have come into contact with Rosemount models before, but I didn’t pay attention to whether they had this feature.
Reply #72017-07-26
I’ve never used Yokogawa, but I’d like an explanation
Reply #82017-07-26
You can check the connection between the sensor and the transmitter

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.