I would like to ask how to adjust the zero point of Siemens’ differential pressure transmitters when measuring negative pressure

2017-08-01View Original

Thread Content

Are there specific steps? Teach me
Reply #22017-08-02
Just like with pressure gauges, the zero point is calibrated in the positive pressure area, and then it can be moved to the negative pressure operating area; this is how we have used EJA transmitters.
Reply #32017-08-02
I have no prior knowledge of Siemens differential pressure gauges. You must check the manual for this table to confirm whether the diaphragm of this transmitter can measure negative pressure! If that’s possible, then calibrating the zero point doesn’t seem very difficult to me.
Reply #42017-08-02
This post was last edited by QQ_9E0F93 on 2017-8-2 at 16:17. What is the range?
Reply #52017-08-02
The second floor is the correct choice. If negative migration has already occurred, then revert to the original state, set the air conditioner to zero, and only after that proceed with negative migration

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.