Can the valve be controlled directly by a level gauge without using a PID controller?

2017-08-10View Original

Thread Content

As long as it is necessary to prevent water from overflowing in one tank, can the output signal from a level gauge be used directly to control the valve?
Reply #22017-08-10
This is what is usually done; more advanced systems employ level-flow cascade control.
Reply #32017-08-11
It can be achieved by simply using a level switch; when the water level reaches the set point, the switch generates a digital signal to control the start and stop of the valve-type pump.
Reply #42017-08-11
It can be achieved by simply using a level switch; when the water level reaches the set point, the switch generates a digital signal to control the start and stop of the valve-type pump.
Reply #52017-08-11
It can be achieved by simply using a level switch; when the water level reaches the set point, the switch generates a digital signal to control the start and stop of the valve-type pump.
Reply #62017-08-11
Using a level switch directly is the simplest approach.
Reply #72017-08-11
To allow the liquid level to fluctuate within a specified range, use a level switch – it is cost-effective, simple, and reliable.
Reply #82017-08-11
Add a 220V solenoid valve to the water inlet pipe, and install a level switch on the inner wall of the tank. With 2*1.5mm cables, the cost is very low.
Reply #92017-08-11
Using a level switch works, but it might not be possible to control the control valve directly with the output of a transmitter, as it is not possible to set a setpoint.
Reply #102017-08-11
The liquid level in many pools and tanks is controlled in this way; a complete set of liquid level valves costs around a hundred yuan. :lol

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.