There are several electric float level gauges that transmit data to the DCS system via safety barriers; the readings shown by these gauges fluctuate. A 24V switching power supply has been replaced, the safety barriers have been checked, and the grounding system has also been inspected. Process-related issues have been ruled out, and interference is suspected as the cause, but the source of this interference cannot be identified. Please help analyze what might be causing this problem.
Reply #22017-12-04
What medium? Specify whether heating is provided and what form the heating takes
Reply #32017-12-04
The measuring medium is oil. No heat tracing
Reply #42017-12-04
Is the selection of the safety barrier correct? Check the safety barrier again
Reply #52017-12-04
Going directly to the card terminal without going through the safety barrier – it’s the same in this case as well
Reply #62017-12-04
So frequently, connect a multimeter in series to measure and see if there is a significant change
Reply #72017-12-04
It’s not that safety barriers cannot be used; in cases where they are necessary, it is recommended to use isolated safety barriers
Reply #82017-12-04
The change in current is consistent with the change in trend
Reply #92017-12-04
There is still an overall trend, but there are interfering factors; identifying the source of these interferences will resolve the issue
Reply #102017-12-04
A float is a variable buoyancy type level gauge; it’s not suitable for measuring oil, right? The viscosity and density of oil have too great an impact on the measurement
Reply #112017-12-04
In your case, it goes into the DCS through a safety barrier, and the safety barrier itself has isolation functionality

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.