I would like to ask experts for advice: How should the MCC cabinets, DCS cabinets, UPS units, thermal control power supply cabinets, and CEMS cabinets be arranged in a denitration system?

2017-12-28View Original

Thread Content

I would like to ask experts how the MCC cabinets, DCS cabinets, UPS units, thermal control power supply cabinets, and CEMS cabinets should be arranged in a denitration system – is it possible to place them all in the same room?
Reply #22017-12-28
Under normal circumstances, the CEMS cabinets should be placed near the measurement points, while the MCC cabinets, UPS units, and thermal control power cabinets should be located in a separate room, and the DCS cabinets should be in another room.
Reply #32018-01-03
Can the thermal control power cabinet be placed in the CEMS chamber, or together with the DCS?
Reply #42018-01-03
Try to avoid being in the same space to prevent electromagnetic interference. There’s really no place to divide the room into two usable sections.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.