Double-flange transmitter 110% above range

2017-03-11View Original

Thread Content

Because the flange was damaged, it was sent back to the manufacturer; after it was installed and put into use, an out-of-range error occurred. Using a BT200 to check showed that everything was the same as before, with no changes. Is the top and bottom reversed? It’s still the issue with the silicone oil; there’s definitely nothing wrong with the surface – it’s still in use or was bought new
Reply #22017-03-11
Is it new, or was it a broken one that was repaired? Was it verified before installation? Are the range and negative drift set correctly?
Reply #32017-03-12
Check if the zero point is correct and whether the range setting is proper
Reply #42017-03-12
The range is incorrect; reset the range to proceed with the migration
Reply #52017-03-13
It is recommended to proceed in this way,:D
Reply #62017-03-13
The most likely cause is a problem with migration; when installing with double flanges, migration should be carried out after the flanges are in place, and the gauge should read zero before the pressure-taking valve is opened.
Reply #72017-03-13
First, perform individual calibration of this instrument before installation; place the double-flange capillary on the same plane for inspection. If there are issues, perform zero-point calibration and conduct an installation check. At the same time, check whether there are issues such as diaphragm box deformation or oil leakage on the flange surface

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.