Is this the correct way to calculate for thermocouples?

2018-02-03View Original

Thread Content

The ambient temperature at the site is 10 degrees, while it is 20 degrees in the control room. The voltage measured at the site is 4.3 mv; should the compensation temperature be calculated based on that of the control room? Is the final result 124 degrees?
Reply #22018-02-03
You need to check what the calibration value of the thermocouple is; if you use a compensation wire, then you don’t need to worry about this
Reply #32018-02-03
In principle, by using a compensation wire, the cold end of the thermocouple is moved from the field location to the end of the compensation wire; the final measurement result is therefore the temperature corresponding to the mV value plus the temperature of the cold end. Modern DCS systems perform automatic compensation.
Reply #42018-02-03
What I mean is, during on-site inspections, after measuring the voltage at the site with a multimeter, should the control room temperature or the ambient temperature at the site be used in the calculations?
Reply #52018-02-03
The key is to determine where the end of the compensation wire (or the compensation device) is located; if it is in the control room, then the temperature of the control room should be taken into account.
Reply #62018-02-03
On-site, the entire premise was designed and constructed correctly
Reply #72018-02-03
Why did the person ahead say to adjust the control room temperature
Reply #82018-02-03
Should it be the control room temperature or the ambient temperature?
Reply #92018-02-04
The temperature value corresponding to the mV value measured at the end of the compensation wire, plus the room temperature at that end position. I was busy with other things just now and didn’t notice that you were measuring the voltage in millivolts on-site. Sorry!
Reply #102018-02-04
The mV value measured at the end of the compensation wire + the room temperature at the location of that end. I was busy with other things and didn’t notice that it was the mV value measured on-site; my apologies! Replies on mobile need to be approved; please reply again using a computer.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.