How to restore the original data of the cumulative values in the DELTAV system

2017-07-18View Original

Thread Content

In our factory’s DELTAV system, a sudden power outage caused the cumulative values of some measuring instruments to be reset automatically. How can we restore the original data of these cumulative values?
Reply #22017-07-20
I’ve encountered similar problems; if the power goes out, all the online data is lost. Personally, I think it’s impossible to restore.
Reply #32017-07-20
Is it from the instrument itself or from the upper-level system? If it’s the instrument itself, check the manual; only those equipped with a backup battery can retain cumulative data. Otherwise, it will be impossible to restore that data, and one can only rely on the system’s curve records.
Reply #42017-07-20
In modulel, the real-time data of the cumulative function block was lost, so accumulation has started over again.
Reply #52017-07-20
Thank you! Our plant uses FF instruments; the field instruments do not have an accumulation function, as accumulation is handled by the DCS system.
Reply #62017-07-20
Thank you! Our factory uses FF instruments; the field instruments do not have an accumulation function – accumulation is handled by the DCS system. It is understood that this can be modified by adjusting the configuration parameters of the DCS, but I’m not sure how to do it.
Reply #72017-07-21
We also use FF instruments. It’s not possible to accumulate points yet; we need to check whether the parameters of the score function block are correct, and also examine the parameters of the date and time function block. The configuration method should be similar

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.