HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Does zeroing a double-flange differential pressure level gauge require changing the upper and lower measurement limits?

2018-02-03View Original

Thread Content

For a double-flange differential pressure level gauge with a capillary, when calibration is required, does it suffice to loosen the upper and lower flanges to expose it to the atmosphere in order to perform the calibration? If the lower measurement limit set in the parameters is negative, is it necessary to shift it to 0 first and then zero it out? ? ?
Reply #22018-02-03
It’s a double-flange differential pressure level gauge with capillaries; it has experienced negative drift and is no longer accurate, so it needs to be recalibrated. Is it necessary to remove both upper and lower flanges, place the gauge in a horizontal position to perform the calibration, and then reinstall them before adjusting the setting again? Is it possible to loosen the upper and lower flanges, allow air to flow in, and then perform zero calibration? If so, how does this calibration process work – is it simply enough to adjust the value to zero? Is it necessary to shift the zero point to zero first and then perform zero calibration?
Reply #32018-02-03
This post was last edited by 1111111 on 2018-2-13 at 15:34. Little buddy, after the migration, the meter’s readings became inaccurate again; so just carry out the migration once more… The range span remains unchanged.
Reply #42018-02-03
If there’s nothing wrong, ask the master for more guidance and learn on the spot, haha
Reply #52018-02-04
Close the upper and lower valves, open the vent, and adjust the zero point
Reply #62018-02-04
The double-flange differential pressure level gauge with a capillary has experienced negative drift; it is no longer accurate and requires recalibration to zero. Before closing the valve between the upper and lower flanges, loosen the flange screws and zero the device after it is connected to the atmosphere. Check what the static pressure difference is; this pressure value represents the negative migration amount. The range should be specified in the instrument’s data sheet – the negative migration value corresponds to the lower limit, while the range minus this migration amount gives the upper limit. Re-entering the values into the instrument will allow for the adjustment to be completed.
Reply #72018-02-04
If calibrating the instrument, such as its accuracy, it is necessary to remove it for inspection and zeroing. If the fault is to be addressed on-site, there is no need for disassembly; simply release the pressure to the atmosphere, then check whether the displayed pressure matches the set value. If it does not, the setting needs to be adjusted again.
Reply #82018-02-04
Close the upstream and downstream valves, disconnect from atmospheric pressure; the gauge pressure should read 0%, which is the lower limit of the range, with the upper limit being the sum of this value and the range width.
Reply #92018-02-04
Bro, when it comes to the zero point of calibration, does 0 KPA refer to the actual zero point, or does it mean that the lower limit of measurement is zero?
Reply #102018-02-04
1. Zero the double flange before installation. (According to the designed medium density) 2. Yours is a field gauge; of course, calibration on-site gives the most accurate results. {Opening it at the top and bottom affects the atmosphere; just set the zero point directly – what’s the need for any adjustment value? There’s no need to calculate it; if one does calculate it, the result should be more or less the same.} 3. If it’s still not accurate, ask the process team (or Sinochem) for the actual density of the medium, calculate accordingly, and then adjust the range accordingly.
Reply #112018-02-04
The 0 position of the level gauge, the starting point of the level gauge.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.