Thread Content
The company has newly purchased a batch of control valves. During the incoming inspection, it was found that the protection rating (IP**) was missing from the label on the actuator, although such a rating is specified in the data sheet. Question: 1. Is the valve acceptable? 2. If it cannot be accepted, what is the legal basis for labeling it on the equipment?
First, inquire with the manufacturer about the protection rating of the products upon arrival and request official written certification documents. Then, it is checked whether the protective structure of the delivered products meets the specifications specified in the certification documents. If it does not meet the requirements, return or exchange will be processed in accordance with the business terms and relevant technical agreements. In case of disputes, apply for inspection by the commodity inspection authority; have relevant professionals conduct the inspection and issue a ruling.
Not accepted. First, check the technical agreement and business contract; if there are relevant requirements in them, demand that the manufacturer refund or replace the product and provide compensation in accordance with the terms of the contract. The design data sheet already requires a protection rating; I’m not sure what legal basis you are looking for.
Not accepted. First, check the technical agreement and business contract; if there are relevant requirements in them, demand that the manufacturer refund or replace the product and provide compensation in accordance with the terms of the contract. The design data sheet already requires a protection rating; I’m not sure what legal basis you are looking for.
GB/T 13306-2016 \"Signs\"
Regulations requiring the indication of the device’s protection rating on its nameplate
It is recommended to adopt the views from the first and second floors.
There must be markings; otherwise, during future safety inspections, it will have to be replaced.
The absence of a nameplate is definitely unacceptable; even if a nameplate is present, it is unacceptable if it does not match the design documents. The design documents serve as the basis, and there is no need to look for any other sources of reference.