Question: Issues with E+H Prowirl 200 series FF bus vortex flow meters

2018-03-16View Original

Thread Content

Question: Issues with E+H Prowirl 200 series FF bus vortex flow meters. DCS: Zhejiang University Zhongkong. The on-site meter display shows a normal value of 2.5 cubic meters per hour, while the FIELD_VAL value of the AI module in the FF hardware configuration is only around 0.0007. Why must out_scale be set to 360,000 for the PV value of the central DCS to match the display on site? ?
Reply #22018-03-16
When the FIELD_VAL value of the AI module in the FF hardware configuration is around 0.0007, what is the value of the out_scale setting? ?
Reply #32018-03-16
This post was last edited by RZT4007110 on 2018-3-16 at 15:40. Regardless of the value set for out_scale, when the volume on site is around 2.5 cubic meters, the FIELD_VAL value is around 0.0007; when the volume is around 1 cubic meter, the FIELD_VAL value is around 0.00027.
Reply #42018-03-16
Oh, I haven’t worked with FF meters yet, but the menu interface in this picture seems a bit similar to that of HART meters. FF meters should also have access testing functions, right?
Reply #52018-03-18
Please try changing L_TYPE to direct or direct independent range
Reply #62018-03-18
It doesn’t matter if it’s changed; whether it’s direct or indirect, it makes no difference. However, if the variable is changed to temperature, it will switch between Celsius and absolute temperature.
Reply #72018-03-18
The main purpose of the L_TYPE parameter is to select between direct, indirect, or indirectly squared root signal conversion. When the poster selects a certain range in OUT_SCALE, the data matches, which suggests that a linearization transformation may have been applied. Since FF is digital communication itself, it is recommended to try it directly.
Reply #82018-03-18
I suggest you make the following changes and try again: First, change XD_SCALE to the range you need, such as 0-50 m3/h. Second, also change OUT_SCALE to 0-50 m3/h. Third, change L_TYPE to directly
Reply #92018-03-18
The last edit to this post was made by RZT4007110 on 2018-3-18 at 17:24; the value of L_TYPE was changed, and the output value became FIELD_Val. It’s possible that there is still some setting issue – I’ll take another look tomorrow :( During the initial debugging phase, I consulted with the after-sales and control system engineers from E+H, and they also set the value to 360,000. Given the high requirements of the process, I didn’t dare make any changes arbitrarily. Recently, another unit was added elsewhere, so I need to learn more about it*:Q
Reply #102018-03-19
It is presumed that the unit of FIELD_VAL is m3/s, and multiplying by 3600 gives m3/h
Reply #112018-03-22
There is a field where the unit for the header should be changed to cubic meters per minute; the DCS range (cubic meters per hour) can only be set to 6000, otherwise it will not match the actual flow rate: L:L. We also suspect it’s a setting issue on the device, but it can’t be 360,000 either – it’s not a multiple of either hours or seconds, nor of milliseconds.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.