Power supply issue

2020-04-27View Original

Thread Content

Help! ! I would like to ask the experts here about a phenomenon I’m experiencing. I use a four-core cable to connect from a 380V circuit breaker (only the neutral wire is connected, no ground wire). Since the cable is too short, I use a five-core cable with an aviation plug (32A) for the connection. When I check inside the distribution cabinet, there’s a problem: when I measure the output terminal of the distribution cabinet (16A), there is a voltage of 280V between the ground wire and the live wire. There’s no problem when I use only a four-core cable to connect to the cabinet. Nor is there any issue when I use a five-core cable and connect it directly to the circuit breaker, including the ground wire. Is it because the presence of a ground wire in the five-core cable creates an interference circuit? Could someone please explain the principle behind this? Thank you.
Reply #22020-04-28
I didn’t quite understand what the original poster meant, nor did I see any pictures; I guess it might be induced electricity? Try it with a small load first
Reply #32020-05-02
Grounding issue. There is a potential difference between the grounding at the power supply side and the grounding at the load side.
Reply #42020-05-02
Any unused conductors in the cable should be grounded; otherwise, induced voltage will occur.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.