There is an orifice plate flow meter on the main pipeline of the low-pressure steam network in the facility; from there, numerous pipelines branch off to various processes. When all processes are using steam, the reading on the main orifice plate flow meter remains almost unchanged, even after shutting down one of the processes that consume the most steam. The orifice plate flow meter transmitter is in good condition with no damage. What could be the reasons for this?
It’s possible that after one circuit was shut down, the air consumption of the other circuits increased, so the flow rate remained roughly the same.
In this case, it is necessary to check whether there is any change in pressure after shutting off the steam supply for a certain process It is also necessary to see what the ratio is between the amount of steam used along the closed path and the total amount of steam
This depends on the ratio between the master table and the subordinate tables; after one of them is disabled, the ratio between the master and subordinate tables changes, and it’s necessary to wait at least a few hours before obtaining accurate statistics.
It is possible that the total gas consumption remains largely unchanged after closing the back route; it is best to determine the gas consumption of each individual branch.
Does it have temperature and pressure compensation? It should be compared under standard conditions
The orifice plate limits the flow rate; if one more pipe is used for gas supply, the flow rate exceeds the measurement capacity of that orifice plate. In other words, just using one additional pipe for gas supply is enough to cause this issue
If you close one gas branch, and if the valve isn’t used to regulate flow, the amount of gas used by the other branches will increase
Looking for other reasons is putting the cart before the horse. When the branch line with the highest gas consumption is turned off, if the total reading doesn’t change, the most likely explanation is that the main meter is inaccurate; any other reasons are merely speculative. It is recommended that the original poster check the instantaneous flow rates of both the main meter and the individual branch meters at the time when the branch valves are closed
Shifang Jiekong Electromechanical Equipment Co., Ltd. http://dyjkjd.com/cpzx/wwyb/29.html The UB500 series of multi-parameter differential pressure transmitters use single-crystal sensors for measuring differential pressure and pressure; they feature excellent overload resistance, automatic temperature compensation. The medium temperature is measured via a 4-20mA input with voltage regulation. An integrated module for measuring differential pressure, pressure, and temperature is built into these transmitters, and various throttling devices and level compensation databases are available to enable automatic compensation for flow rate and level in terms of temperature and pressure. With its high degree of integration, its functionality is equivalent to that of three field transmitters plus one flow meter. It offers long-term stability, high reliability, ease of use, high measurement accuracy, and reduced installation requirements. It is suitable for measuring pressure, differential pressure, temperature, flow rate, level, and density of gases, liquids, and steam. A multi-parameter transmitter mainly consists of four components: a monocrystalline silicon sensor for pressure measurement, a temperature sensor, a measurement circuit, and process connectors. It allows for the free definition of 2 output variables with 4-20mA output, and features a MODBUS communication interface for seamless integration with energy metering systems. I. Technical specifications: Pressure measurement range: 0–30 MPa (gauge pressure). Differential pressure measurement range: 0–250 KPa. Medium temperature measurement range: -50–600°C. Accuracy: Class 0.075, Class 0.2. Temperature range for differential pressure and pressure sensors: -10–60°C. Voltage: Standard 24 VDC. Load capacity for 4-20 mA signal: 0–500 Ω. Protection rating: IP68