Reference materials for combustible gas detectors in the petrochemical industry?

2018-06-08View Original

Thread Content

Recently, I’ve encountered several Sinopec projects in which the client’s drawings specified that propane or isobutane should be used as the calibration gas for the combustible gas detectors. Some projects even specified an infrared-based detection principle. Although the current CCC certification standards for combustible gases require the use of methane, propane, hydrogen, and carbon monoxide as calibration gases, almost all combustible gas detectors purchased in the past were calibrated using methane. I don’t have much experience in the petrochemical industry. I would like to ask those who are familiar with this sector on the forum: do combustible gas detectors used in the petrochemical industry necessarily need to be calibrated using propane? Is the infrared principle used in all sectors of the petrochemical industry?
Reply #22018-06-08
It is specified that the testing medium should be calibrated using the actual gas to be tested; for general use, isobutane is typically used for calibration.
Reply #32018-06-08
We generally use butane as the testing gas
Reply #42018-06-08
The detector should be calibrated using the same medium that it is designed to detect; for example, a hydrogen sulfide alarm device needs to be calibrated with hydrogen sulfide. Ammonia gas alarm, calibrated using ammonia gas. Our factory uses the same medium for calibration as that which is being tested; for hydrogen sulfide, the principle involved is electrochemical, while for flammable gases, it is catalytic combustion.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.