What is the most accurate level gauge for measuring the liquid level in a tank with agitation?

2018-10-18View Original

Thread Content

Which level gauge is the most accurate for measuring the liquid level in a reactor with stirring? Ignoring costs, pressure of 6 MPa and temperature of 180°C, with a catalyst slurry inside
Reply #22018-10-18
It seems we can only use a level gauge based on nuclear radiation
Reply #32018-10-18
Here, the pressure and temperature are 2.0 and 70 degrees; a nuclear level gauge is being used
Reply #42018-10-18
Is it accuracy or reliability? The medium category also needs to be specified, especially in cases of corrosion, crystallization, etc
Reply #52018-10-18
For accurate and reliable measurements, it is also necessary to know the size of the reactor, the corrosiveness of the medium, whether crystallization occurs, whether explosion protection is required, and the density of the medium; merely knowing the pressure and temperature is not sufficient to provide meaningful insights.
Reply #62018-10-18
1. What is the size of the tank? What is its diameter and height? 2. The main chemical components of the liquid material need to be clearly specified. It should be clearly stated whether crystalline scaling occurs, or whether solidification takes place upon cooling. 3. If price isn’t a concern, come to me for a custom order – I’ll design a special level gauge for you that is resistant to stirring and high temperatures, and whose sensor diaphragm doesn’t come into contact with liquids. Bro will provide a level gauge that is reliable and easy to use, just like your water gun – it will follow your instructions and won’t fail or become weak. :lol
Reply #72018-10-19
It would be best to provide a diagram showing the size of the reactor and the size of the stirrer blades
Reply #82018-10-21
Why not use the weighing method? ? ? Choosing a radar is another option; filter algorithms can be used to eliminate the interference caused by stirring.
Reply #92018-10-22
If the liquid is not viscous and does not crystallize, various types of level gauges can be used, such as radar or double-flange type gauges; if it is viscous, then nuclear or external-mounted level gauges have to be considered
Reply #102018-10-24
This post was last edited by ssln123 on 2018-10-24 at 16:06. The requirements for managing nuclear radiation are high, and the problems become even greater if there are multiple reactors. I’m facing the same problem as the original poster: the reactor has a stirrer, the temperature is high, and the medium is viscous; therefore, the level gauge can only be installed at the top. The design team recommended a pulse radar, but it doesn’t work effectively within a range of about 2 meters, so I assume there will be significant fluctuations in that area.
Reply #112018-10-25
Still the same question: what is your mixing speed, and what level of liquid do you want? When stirred, the liquid surface isn’t level

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.