Which level gauge is the most accurate for measuring the liquid level in a reactor with stirring? Ignoring costs, pressure of 6 MPa and temperature of 180°C, with a catalyst slurry inside
It seems we can only use a level gauge based on nuclear radiation
Here, the pressure and temperature are 2.0 and 70 degrees; a nuclear level gauge is being used
Is it accuracy or reliability? The medium category also needs to be specified, especially in cases of corrosion, crystallization, etc
For accurate and reliable measurements, it is also necessary to know the size of the reactor, the corrosiveness of the medium, whether crystallization occurs, whether explosion protection is required, and the density of the medium; merely knowing the pressure and temperature is not sufficient to provide meaningful insights.
1. What is the size of the tank? What is its diameter and height? 2. The main chemical components of the liquid material need to be clearly specified. It should be clearly stated whether crystalline scaling occurs, or whether solidification takes place upon cooling. 3. If price isn’t a concern, come to me for a custom order – I’ll design a special level gauge for you that is resistant to stirring and high temperatures, and whose sensor diaphragm doesn’t come into contact with liquids. Bro will provide a level gauge that is reliable and easy to use, just like your water gun – it will follow your instructions and won’t fail or become weak. :lol
It would be best to provide a diagram showing the size of the reactor and the size of the stirrer blades
Why not use the weighing method? ? ? Choosing a radar is another option; filter algorithms can be used to eliminate the interference caused by stirring.
If the liquid is not viscous and does not crystallize, various types of level gauges can be used, such as radar or double-flange type gauges; if it is viscous, then nuclear or external-mounted level gauges have to be considered
This post was last edited by ssln123 on 2018-10-24 at 16:06. The requirements for managing nuclear radiation are high, and the problems become even greater if there are multiple reactors. I’m facing the same problem as the original poster: the reactor has a stirrer, the temperature is high, and the medium is viscous; therefore, the level gauge can only be installed at the top. The design team recommended a pulse radar, but it doesn’t work effectively within a range of about 2 meters, so I assume there will be significant fluctuations in that area.
Still the same question: what is your mixing speed, and what level of liquid do you want? When stirred, the liquid surface isn’t level