Samson 3730-3: After the intelligent locator is initialized, the valve oscillates – how to adjust the parameters?

2018-07-26View Original

Thread Content

There are too many instructions, and no parameters seem to be available for adjustment
Reply #22018-07-27
I encountered this issue once before as well; the valve position kept fluctuating. After checking the manual, I found a gain setting, and increasing its value resolved the problem. You might want to give it a try to see if it works
Reply #32018-07-27
This is a regulator with built-in proportional-integral control; since oscillations are mainly caused by the integral term, adjust the integral setting first. If oscillations cease, check the static error – if it is still large, then adjust the proportional setting
Reply #42018-07-27
The instructions say to adjust codes 17 and 18, but I haven’t had time to verify it yet; let’s see if there are any other options
Reply #52018-07-27
Right, I saw the instructions last night. Are there any other options?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.