How do I perform migration for this single-valve level gauge? The distance from the valve gland to the gauge head is 30 centimeters. The total height is 1.9 meters. Urgently need the amount to be migrated. Which expert can help calculate this? Thank you
Reply #22018-05-05
Newcomers, come and take a look; learn*learn*
Reply #32018-05-05
This post was last edited by ssln123 on 2018-5-5 09:36. Negative migration: the density of the silicone oil in the capillary *9.8*0.3 gives the amount of migration, which is also the differential pressure shown when the tank is empty before migration occurs.
Reply #42018-05-05
Is this just a flexible pressure guide tube? So what happens when the liquid level drops below the transmitter’s position?
Reply #52018-05-05
Oh, is this a Rosemount transmitter?
Reply #62018-05-05
1. Single flange design: the low-pressure chamber of the differential pressure gauge is connected to the ambient atmosphere, while the gauge itself is installed 30 centimeters higher than the sampling point? ! :Lol, damn it – this is an incorrect installation! . . . What the hell is there to migrate? Migrate it already. 2. Obviously, when (P_liquid – P_oil) ≤ 0, the reading of the differential pressure gauge remains constant at 0. So can you clarify whether the zero liquid level corresponding to this zero differential pressure is located above the sampling point? 3. Differential pressure gauges cannot be installed in this way in open tanks; the gauge itself must be lowered to a level lower than that of the fluid level measurement point. This ensures that the physical zero liquid level corresponds to the measurement point, and it guarantees that the height of the liquid column above the zero level is directly related to the differential pressure value. Only then does moving the differential pressure gauge have a physical basis. :lol
Reply #72018-05-06
What kind of migration volume is that? You don’t even explain clearly what kind of silicone oil is used inside; anyway, it’s pointless. The simplest method is to install it, tighten the bolts, enter the measurement range, and then set the zero point once more at that time!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.