How can there still be flow if the flow meter is frozen?

2018-12-10View Original

Thread Content

The weather is cold tonight. At first, the steam flow meter showed a stable reading; then, when the steam control valve was adjusted to its original setting, the steam flow increased. The normal flow rate is 16,000 t/h, but it has now risen to 26,000 t/h. It is suspected that the flow meter has frozen. I went to the site and used steam to heat the flow meter, and the flow rate returned to 16,000 t/h. If the meter is frozen, the flow rate should indicate 0 t/h – so why did it increase?
Reply #22018-12-10
It depends on the type you’re using. If it’s a differential pressure type that freezes, there will be pressure on both the positive and negative sides, and definitely a flow rate display will be available; it’s just hard to say what the value of that display will be
Reply #32018-12-10
A flow rate of 16,000 t/h – what size boiler would that require? How thick is the pipe! !
Reply #42018-12-10
With such a large amount, it expands, and that’s why. . . . Insulation is not properly done
Reply #52018-12-10
The flow meters for steam will freeze up; the instruments either don’t respond or show the full scale value or 0
Reply #62018-12-10
If it is because the pressure tap pipe has frozen, the flow rate may increase or decrease.
Reply #72018-12-10
When the pressure tap pipe freezes, its volume expands, which continuously exerts pressure on the transmitter; over time this can damage the transmitter. In the case of the positive pressure pipe, severe freezing leads to an increased flow rate, while severe freezing of the negative pressure pipe results in a lower flow rate or even a negative value.
Reply #82018-12-11
You can study the working principles of various instruments, and then you’ll understand it naturally – the type you’re using is for differential pressure measurement, right? When it freezes, ice creates pressure on the transmitter; of course, there’s also flow involved
Reply #92018-12-11
You’re using a differential pressure flow meter for measurement, right? The pressure guiding tubes have frozen; ice creates pressure on the transmitter, and as a result the flow rate may increase or decrease. The main issue is poor insulation.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.