Single-unit debugging of Fisher intelligent locator

2018-12-25View Original

Thread Content

There is no DCS; there is a 24V power supply, a signal generator, and a 475 handheld controller. How should the wires be connected to enable communication and calibration?
Reply #22018-12-25
The signal generator provides an active 4–20 mA signal; by connecting a gas source, communication using 475 is possible
Reply #32019-03-12
You can simply connect it directly to the power supply using a handheld controller; if a connection cannot be established, a 250-ohm resistor can be inserted in the circuit.
Reply #42019-03-13
Don’t transmitters not require a 250-ohm resistor?
Reply #52019-03-13
The second floor is correct; using a signal generator, communication is possible without a 250-ohm resistor. However, if a 24V power supply is used directly, a 250-ohm resistor is required

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.