What happens to the interlocked shut-off valve when the purge air stops?

2019-01-04View Original

Thread Content

Are cut-off valves also divided into open and closed types?
Reply #22019-01-04
The shut-off valves in critical areas are equipped with their own independent air tanks, which allow for some time to be gained; even when the air supply is cut off, pressure is not lost immediately, as the buffer tanks at the inlet of the system still provide a period of time for operation~~~
Reply #32019-01-04
Of course, there is a switch to turn the wind on and off. Lift the cylinder and turn the valve core 90 degrees, and it changes.
Reply #42019-01-06
It depends on the operating principle of your shut-off valve
Reply #52019-01-07
According to process requirements, cut-off valves can operate in an open state when air is lost or in a closed state when air is lost. So there will be changes.
Reply #62019-01-07
Consider wind pressure, switch speed, and valve selection; sometimes it’s necessary to make distinctions, while other times it isn’t
Reply #72019-01-07
It can be separated; what will happen when the air purification is stopped? Depending on the characteristics of the valves, the air flow will either be turned on or off
Reply #82019-01-07
Check the nameplate: FC, FO, FLO, FLC
Reply #92019-01-08
When the purification air supply to the device is stopped, the FC valve closes; when air flow is enabled, it opens. In case of a fault, it closes. The FO valve closes when air flow is stopped, and it opens in case of a fault, with the valve fully open. FC/FL: Wind open/hold position; instrument air is stopped, and the valve remains at the opening degree it had just before that, until the hold-position valve fails for various reasons, after which the valve closes. FO/FL: Wind closed/hold position; the opposite of the above.
Reply #102019-01-17
In practical applications, when the instrument air is interrupted, even in the absence of a gas storage tank, the pressure in the pipeline network does not drop to 0 immediately. Therefore, unless an interlock is triggered, the valves will remain in a state of uncertain opening degree for some time.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.