HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Orifice plate flow meter

2019-03-01View Original

Thread Content

Continuing with the issue from the previous two days: the maximum flow rate is 5 tons, the rated flow rate is 10 tons, the range of the differential pressure transmitter is 0–25 kPa with an internal setting of 10 kPa. The current actual flow rate is 13 tons. I would like to know if this can be adjusted using the transmitter The orifice plate still needs to be replaced
Reply #22019-03-02
This post was last edited by Concave Blade Hero on 2019-3-2 at 10:17. Replacing the orifice plate is rather troublesome, and it also requires that the process conditions permit it. Is the differential pressure value of the differential pressure transmitter outside its range? If not, then there’s definitely no problem
Reply #32019-03-02
1. First, the setting of the maximum range is unreasonable. The process parameters set are simply ridiculous; I remember saying a few days ago that the normal value was 3 and the maximum value 5. Now, however, the normal value is 13. It’s clear that the orifice plates chosen earlier were not suitable, or they exceeded the specified requirements, with their precision and uncertainty far exceeding acceptable levels. 2. The on-site transmitter and the indoor setup must be consistent; can accurate measurements be taken if they are not? 3. Regarding your question, it can be adjusted through the transmitter, but the problems that arise are as mentioned in point 1. It is recommended to recalculate; if it no longer meets the specification requirements, it is suggested that the process team provide more accurate parameters for recalculation and selection.
Reply #42019-03-02
The range of the differential pressure transmitter can be increased; the flow rate can be calculated by using the formulas provided in the orifice plate calculation sheet with the increased range
Reply #52019-03-02
The modulator transmitter is useless; it needs to be recalculated
Reply #62019-03-12
The flow rate has now exceeded the rated value, so the orifice plate needs to be recalculated. If precise measurement is required, the orifice plate needs to be recalculated; as long as a certain number is available and the orifice plate is safe at that flow rate, the range of the transmitter can be increased accordingly.
Reply #72019-03-12
Recalculate; stop doing those useless things……
Reply #82019-03-14
The data calculation is performed again; it’s still the same orifice plate, and the resulting differential pressure value is then adjusted by the transmitter
Reply #92019-03-14
The orifice plates must be recalculated; the size of each opening and its angle are determined through calculations. Otherwise, the measurements obtained will not be accurate at all, and they cannot even be used as a reference. Transmitters are no longer important; if the original measuring device is inaccurate, then no matter how high the transmitter’s precision is, it’s of no use – it only serves to increase the error. Therefore, the orifice plate must be replaced; the transmitter can continue to be used by adjusting its range.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.