2019-03-27View Original

Thread Content

When the flow rate is 0, the on-site instrument shows 0, but when measured with a multimeter, there is a current of 4.04 mA. How can this current be reduced to 4 mA or below? It doesn’t help to turn off the flow at low levels; it’s also useless to set the value to 4 mA at low flow rates, and resetting it to 0 doesn’t work either. I’m not sure what will happen if a very low flow rate is used to reset it to 0
Reply #22019-04-01
It’s been replaced; it’s not a problem with the multimeter!
Reply #32019-04-19
If the flow meter is functioning properly, set the small-signal cut-off percentage to a slightly higher value
Reply #42019-04-19
Your flow rate shows 0, and the reading on site is also 0. You can use a HART connection to view the specific data inside. If you find that 4.04 mA is not acceptable, you can either disable the low-flow signal or perform zero-point calibration; however, even after zero-point calibration, there will still be slight changes in current flow, and it’s impossible for it to stay at 4 mA
Reply #52019-04-19
There’s absolutely no problem with yours; the normal output current is 4 milliamps, and there are also some variations in the device’s output. Your value of 4.04 milliamps falls within the acceptable range, so there’s no issue at all.
Reply #62019-04-19
Check the manual: zero it out when the tube is full. If that doesn’t work, look for a zeroing knob. If that still doesn’t work, replace the circuit board

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.