Connection of motor signal wires

2019-06-04View Original

Thread Content

How do the motor’s feedback signals get into the instrument cabinet?
Reply #22019-06-04
Check whether there is any unwanted voltage on the feedback signal line; if so, a relay can be used for isolation
Reply #32019-06-04
Select the contacts from the electrical secondary circuit diagram. Connect the contact to the instrument system and add a relay.
Reply #42019-07-28
AC contactors, or electrical drawer cabinets – in any case, isolation is required.
Reply #52019-07-28
Relay, or safety barrier isolation, IO card in the cabinet
Reply #62019-07-29
Digital signals (dry contact, level signal), isolated input to relay; Analog signal (4~20mA) with isolation barrier.
Reply #72019-08-17
The motor’s status signals or fault signals are DI signals from the electrical system, which are connected to the relay (it’s a two-core wire connected to the relay; the electrical side operates at 220 volts, so isolation is necessary. Remember that it should be dry contacts – meaning there is no voltage on the wire coming from the electrical side, only connections and disconnections). As for the signal indicating the current level of the motor, it is a 4-20mA current signal transmitted from the electrical system, which is then sent to the corresponding safety gate.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.