PLC power supply failure

2019-06-06View Original

Thread Content

During the recent thunderstorm season, the night before yesterday. There is a PLC control cabinet on site. The Mean Well power supply New Well NES-200-24 in the cabinet suddenly lost its 24V output during a thunderstorm. 220V is always present when inputted. So, a new power supply was installed. It's a good idea to take the faulty module back for inspection of the fuse; it also functions normally after being powered on. I wonder if anyone has encountered such a situation
Reply #22019-06-06
This matter ends up being completely worthless. Induced lightning strikes enter through the power grid, starting from the power supply, and cause a series of equipment instruments to be damaged; this is quite common. .
Reply #32019-06-06
Lightning strikes are large voltage spikes that last for milliseconds, or even less time. How large are they? Hundreds of thousands of volts, maybe millions of volts...... The time interval is too short; the fuse doesn’t have time to heat up and blow before the lightning strike passes. So it’s normal for the fuse not to burn out in the event of a lightning strike. . .
Reply #42019-06-06
Grid surges caused by lightning electromagnetic storms lead to automatic power protection or short-term damage. Many electronic components have the ability to repair themselves after suffering an instantaneous overvoltage breakdown, so no fault can be detected afterward. Power supplies that have experienced this will be more prone to problems when faced with surges in the future. Therefore, if it is not due to automatic power protection activation, this power supply should preferably not be used in production equipment anymore.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.