Should the temperature of the three-phase windings of a high-voltage motor be used for alarm purposes or for interlock functions?

2025-03-07View Original

Thread Content

As the title suggests, drawings from typical motor manufacturers will specify the alarm values and shutdown values. Is the shutdown value here the same as the interlock value? I’ve seen many pump and chemical plant manufacturers set this shutdown value to correspond to a high-alarm level; there are also pump manufacturers that use a two-out-of-three interlock system, with temperature measurements taken for each phase – but this approach isn’t very precise. Additionally, some pump manufacturers use a two-out-of-two system for single phases, which is much more reasonable. I’d like to discuss with everyone how people handle this matter – are there any industry standards, or does it entirely depend on the preferences of the project design agency?
Reply #22025-03-07
Typically, the temperature settings for a motor’s three-phase windings are defined at two levels: an alarm value and a shutdown (interlock) value. The alarm value is used to alert operators to the equipment’s condition, while the shutdown value serves as an overheat protection mechanism for the motor; when this value is reached, the motor shuts down to prevent damage. In practical applications, different manufacturers may adjust these values according to specific requirements, such as setting high-high alarms or employing two-out-of-two interlock strategies. Industry standards may vary by region and industry; it is recommended to follow the guidelines of relevant project design institutes or industry standards for design and configuration. .
Reply #32025-05-27
Generally, there are an alarm value and an interlock shutdown value; the machine will shut down as soon as either of these values is reached
Reply #42025-05-28
1 With full consideration for safety, set alarms for winding temperature, and implement interlock in case of single-phase overtemperature. 2 If availability also needs to be taken into account (as shutting down the factory arbitrarily would result in heavy losses), then set up alarms, along with a two-out-of-two or three-out-of-two interlock system.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.