After the E H servo level gauge was put into operation, the output current remained at 22mA. I would appreciate some guidance from experts. Thank you!

2019-08-16View Original

Thread Content

After the E H servo level gauge was put into operation, the output current remained at 22mA. I would appreciate some guidance from experts. Thank you!
Reply #22019-08-16
Is there any feed? If not, try injecting some water to see if the level will start counting from zero once it increases. I’m not sure if E+H will work in the same way as its radar – it’s possible to set the alarm level to its maximum when there’s no content in the tank. You can also check the parameter settings to see whether the alarm display shows the maximum value
Reply #32019-08-17
22Ma: This is the magnitude of the output current that remains after the instrument itself has detected a fault code. Check whether there is an interlock HART handheld device to see if any error messages are available
Reply #42019-08-19
Check if an alarm has been triggered; if not, examine the current output settings
Reply #52019-08-20
If it’s an empty can, then an overload alarm is completely normal.
Reply #62019-09-03
What is the actual liquid level? Many customers report problems in this way: they only state the result, but do not provide details about the actual operating conditions, making it impossible to determine the issue.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.