Adjustment of the temperature measurement range for K-type thermocouples.

2019-08-24View Original

Thread Content

For a K-type thermocouple with a temperature range of 0 to 500 degrees, what is the current when the temperature is set at 100 degrees? But the PV value shows around -27.
Reply #22019-08-25
Is the thermocouple wired backwards? The preliminary judgment is that the wiring is incorrect.
Reply #32019-08-25
This post was last edited by 659zhulinfeng on 2019-8-25 at 22:18. The current corresponding to 100 degrees should be 4 + 16 * (100 + room temperature; if the temperature at the temperature compensation point is around 20 degrees), / 500 = 7.8 mA. Often, the minimum current set by the transmitter is 3.8 mA. An alarm is triggered if the value is below this level. There could be several possible reasons for this; please consider the following: 1. Is there a problem with the thermocouple? If the temperature is 100 degrees, remove the compensation wire and measure the potential of the thermocouple. 2. Could there be an issue with the temperature sensor itself? 3. Is there a problem with the safety barrier? Try swapping it with other temperature safety gates. 4. Connect the compensation wire in reverse

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.