Why is the Mondus communication intermittent when displayed on DCS?

2019-07-30View Original

Thread Content

Why is the Mondus communication intermittent when displayed on DCS? Is it a problem with the communication module?
Reply #22019-07-30
At that time, the com2 communication stopped working; it was restarted
Reply #32019-07-31
I have used MODBUS communication in over a dozen cases, and such a situation has never occurred. 1. Check the quality of the communication lines and whether the shielding is proper Condition of wire tightening. 2. Is the communication load too high? 3. Is the communication baud rate set too high? 4. Is the equipment properly grounded?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.