AVP100 feedback rod installation issue

2019-09-18View Original

Thread Content

As shown in Figure 2, the feedback rod above the cylinder is normally installed at a 90° perpendicular angle to these two straight lines, ensuring normal operation of the cylinder. However, the cylinder of the other device is installed vertically at 90° as shown in Figure 1, and can only be in the fully open or fully closed position. But it’s fine if the feedback forms a 120° angle in the direction of the green line. What causes this?
Reply #22019-09-18
The linear feedback rod is at a 50% opening level. For angular travel, it depends on the initial angle position; 50% opening corresponds to an initial angle of 45 degrees.
Reply #32019-09-19
I agree with the view from the second floor: for control valves with angular travel, when installing a positioner, a 50% valve position signal is usually provided; the valve position is adjusted manually to around 50%, and then automatic calibration is carried out (for intelligent models).

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.